3000/120 multiplus charging at 64.9amps

Hi,


My multiplus is connected to 3x200ah victron lifep04 batteries and only charges at 64.9 amps max. I have 2kw of solar running through victron MPPT Charge controllers and multiplied comes up with a total of the solar input plus the 69.4a from. The multiplus. My multi control is set to 16a.


Why am I only getting the 64.9a from the multiplus. I'd prefer 120a

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
gmd avatar image
gmd answered ·

Check with CONFIGURE how the the charge current is set for your unit.
Your 600 Ah should take more than that and it will work when configured correctly.
I had this issus until I realised that I had limited the charge current of my parallel multies.
Hope this was the reason.|
Regards

Gmd


2 |3000