Parallel Multiplus 12/3000 120-16 and12/3000 120-50 poosible?

Hello, is it possible to parallel a Multiplus 12/3000 120-16 which is since two years in use with a new multiplus 12/3000 120-50 ?

Thank you for Answers!

multiplus in parallel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
markus avatar image
markus answered ·

Hi,

I am sorry this is not possible. The units have to be EXACTLY the same.

See here: https://www.victronenergy.com/live/ve.bus:manual_parallel_and_three_phase_systems

All units in one system must be the same type and firmware version, this includes same size, system voltage, and feature set. The type is indicated by the first four digits of the firmware version number. For details, see the “VE.Bus Firmware Numbering System” section in the VE.Bus Firmware versions explained document.

Regards,

Markus