Battery Monitor [512] - High voltage alarm: Alarm

Just installed a 48v 5kw Multiplus II GX with 4 Pylontech 2.4kwh batteries. After setup the batteries were charged from 70% to 100% the VRM is showing an alarm of High battery voltage. Battery reading 52.29V. Victron energy website shows Max Charge Voltage for this battery as 53.2V. HELP PLEASE



Pylontech
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Merlin

There are several threads on this forum about this topic.

Usually when Pylontech are new this can be an issue. The second one it they don't reach 100% SOC for a few days. It is not that the whole battery voltage is high it will be one or two cells in the pack somewhere that are higher. After a few days and some internal balancing that the pylontechs internal bms system should sort it out.

If it does not then a firmware upgrade I think on the batteries may be the answer.

It has been a while I hope it has sorted itself out already.