I've been unable to find clear information on how to correctly connect the BMS load disconnect to the Phoenix 12/1200. Special cable or just a connection to the right or left remote socket on the inverter?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I've been unable to find clear information on how to correctly connect the BMS load disconnect to the Phoenix 12/1200. Special cable or just a connection to the right or left remote socket on the inverter?
Which Phoenix do you have?
https://www.victronenergy.com/inverters/phoenix-inverter-vedirect-250va-800va
or
https://www.victronenergy.com/inverters/phoenix-inverter-compact
The first one can be controlled with a simple wire at the left contact of the remote connector (manual 3.6).
The second one can be connected to the "Multi/Quattro" port of the BMS with a RJ45 cable.