Can one control charge current in Multiplus depending on weather your grid connected inverter is export power to grid

Can one control charging current in a multiplus to maximise self consumption with a Genius device , Grid connected PV inverter and Energy meter? In principle this is possible - monitor power flow with energy meter and adjust the charging current in the Multiplus using Venus. I do not want to implement ESS for several reasons. I have no need to limit grid tie inverter

MultiPlus Quattro Inverter ChargerVenus GX - VGXEnergy Metercharge current limit
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
jfleissner avatar image
jfleissner answered ·

Hi!

As far as I know you could only do this by "external means". I would use a RaspberryPi running nodeRed and access the necessary modbus registers on the Venus to change the values according to your available excess power.

J.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

PeterM avatar image
PeterM answered ·

Hopefully this facility will be soon be part of the Venus OS. Can all be done in Software