I have a Multiplus 3000 inverter charger and couldn't quite work out from the manual how the max AC input feature worked. I have a 3.8kw diesel generator, so I'll set the AC input limit to 3.4kw. My question is, if the multi is pulling 1.5kw(ish) to charge the batteries and I was to turn say a 3kw dryer on, would this just overload the geni or would the multi cut the battery charging current to allow the dryer to run? Or does the battery assist come into play somehow here? Would appreciate if someone could explain. Also side question, I bought my Multiplus second hand and although looks identical inside and out, the front actually says Multi-G, but can't find anything online about it, so I assume it's the same as Multiplus?