BMV reports alarm at incorrect SOC

Set my LOW SOC alarm on the portal to alarm at 60 % and I get an alarm at 70% . It triggered when discharging from above 70 %. Venus at V2.58


VRMBMV Battery Monitor
1599137528110.png (22.2 KiB)
1599137566673.png (19.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
harold avatar image
harold answered ·


The Alarm on the portal is not the same as on your device and/or GX.

You can adjust the built in alarm values on the unit itself, or in VictronConnect if it has Bluetooth Smart, or via VictronConnect Remote.