Unable to read register 830 - network loss

Unable to read register 830 - grid loss.

I can read other registers well, only 830 does not work.

Has the number of this register changed - grid loss?

Thank you for your help.

Modbus TCP
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

This has changed.

It is now register 64 and unit ID has also changed from 100 to the VE.Bus unit ID.

See the last section in this document here:
https://community.victronenergy.com/storage/attachments/12579-venus-os-firmware-changelog-v260-beta-version.pdf