question

la-vie-en-rose avatar image
la-vie-en-rose asked

DipSwitch Settings on Battery Alarm GX

Now I am a little bit confused with the dip switches. The manual gives an example for the standard settings 24 Volt and a low alarm at 21 Volt.

How to configure the low alarm from 21 Volt to 21,6 Volt ? (or anything between 21,5 and 22 Volt?). The reason is that I run a computer network on my boat and I still need a little bit security time for the power supply.)
alarm
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

With the given examples I would say the reference for 12V is 13.5V and for 24V it is 23V.
So I guess you need to set A2, A3, A5 = ON and the other to OFF to get 21.6V as the alarm voltage.

23V-0,2-0,2-1=21,6

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources