Grafana + Venus + Reference Points

Hi,


Could someone tell me what the difference is between :


solarcharger/Pv/I

and

system/Dc/Pv/Current


I am trying to create a panel that displays the sum of the 2 solar chargers. The issue is that "solarcharger/Pv/I" reports correctly for each instance, but the value retrieved for "system/Dc/Pv/Current" is more than double the cumulative value of the solar chargers?


Venus OSVenus GX - VGXMQTTgrafana
1598095875384.png (57.6 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
Peter Buijs - NL avatar image
Peter Buijs - NL answered ·

It looks like the 50A is the Total PV Charging current of a 48V system

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Peter Buijs - NL avatar image Peter Buijs - NL commented ·

https://github.com/victronenergy/venus/wiki/dbus#solar-chargers

0 Likes 0 ·
insanesplash avatar image
insanesplash answered ·

I see in the manual the setting I have chosen is correct.



I have 2 solar chargers, each limited to 45A. This value does change based on the PV power generated but is not ever equal to the output of both chargers. I suspect this value is not reporting correctly.






1598173745127.png (4.4 KiB)
1598173812376.png (54.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mark avatar image
Mark answered ·

I think you might be confusing PV input current (into the solar charger) with system/Dc/Pv/Current - which is the sum of the output/charge current from the solar chargers.

2573W / 47A = 54.7V, which is a realistic battery voltage for a 48V system (you don't show the battery voltage in your Grafana screen image).

The solar chargers convert power between the PV input and charger output - so the voltage decreases and current increases. Power remains constant, apart from conversion losses.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

insanesplash avatar image
insanesplash answered ·

Thanks Mark. Yes it is a 48V battery system. I see your point. I'll give this some more thought, thank you.


1598248563463.png (62.3 KiB)
1598248739859.png (62.4 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mark avatar image Mark ♦♦ commented ·

No worries...

Double check the path you have linked to North MPPT 'PV I (in)' - in the screen image above it seems like you may have accidentally linked it to system/Dc/Pv/Current since it is showing the same current as 'Total PV Current (out)' and 113V x 9.9A equals alot more than 310W.