AC Coupling with Autotransformer

Hello,

I currently have a 15kw Quattro with a 100A Autotransformer on AC Out 1 to provide power to a distribution panel. I want to attach my solar PV to AC Couple the system. The Quattro and battery size both satisfy the factor 1 rule... What I'm wondering is if I can I attach the PV between the Autotransformer and distribution panel? or does it have to be attached in between the Quattro's AC Out 1 and Autotransformer?

Thanks for any help.


MultiPlus Quattro Inverter ChargerAC PV CouplingAutotransformer
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

The PV inverter should be connected at the distribution panel where the protection devices will be.
Your electrician will be able to advise you on specific local electrical rules.