Hello,
100AH Super Cycle AGM. First time cycling battery was discharged to 76% SOC. Turned on a Renogy 40A DC-DC charger with temperature compensation set to the AGM profile. Smart Shunt was showing voltage at 13.57 and amps at +38. No loads on battery during charging. 38 seems a bit much! Data sheet says low internal resistance and they weren't kidding!
Battery has a stamp on it that says max initial charge of 24A. No literature included with battery and all the data sheets I have found don't specify charging, just use C20 as example for cycle life.
Do I need to install a charger that will not exceed 24A?
Thank you.