Hi I have a job with 6 pylonTech U2000 connected to a MultiPlus 48/5000/70-100 Firmware 459 and Venus GX Firmware v2.60~35. There is a grid meter, 5kW of fronius solar on the output and 5kW of solar on the input to inverter. I have a number of battery issues that could be related and was wondering if anyone had some Ideas.
1. The GX is telling me the charge current limit is 100Amp But if change Current is 25Amps per battery this should be 150Amps. I have tried multiple times and ways to detect batteries but no luck getting the 150Amp limit. is there another way to see what has been detected by the GX?
2. The batteries will not charge at more than 40Amps. Excess power is been exported insted of going into battery so battery is not fully charged some days. What could be limiting charge current?
3. In the ESS I have minimum SOC Set to 0% but the VRM is showing they only discharge to 20%. What could be stopping discharge to 0%? (have tried setting at 10% and 5% but same result)
4. From a indicated 98% to %20 SOC VRM is telling me I am getting best case around 9.5kWh form the battery a day. if the usable capacity of the pylonTech U2000 is 2.2kW I should technically getting 10.5kWh to 20% SOC from 6 batteries so I'm 1kWh short, Is this normal? But alternatively if I only have 4 batteries as indicated buy the charge current limit I should only be getting 7kWh a day. so it looks like I'm doing better than 4 batteries. Is there another way to tell if all the batteries are working OK?
Thanks in advance for any tips on these points
Cheers Jon.