question

Eero Silfverberg avatar image
Eero Silfverberg asked

Generator start/stop autostart conditions not applying

Hi, I have a question regarding the generator auto start/stop function in the Venus OS. Should the generator autostart conditions be applied immediately or does every change of conditions require a reboot. Currently when I change for example the SOC conditions the CCGX needs to be restarted in order to the autostart to work.

Testing setup:

Battery SOC: 92%

Set autostart by SOC: 95%/98%
Relay clicks, State: Running by SOC condition
Change SOC autostart conditions to 85%/98%
Relay keeps being closed and State: Running by SOC condition

Venus OS: v2.60~37

Venus OSGenerator
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

no the device does NOT need to be rebooted to effect the change, HOWEVER please not you are using Beta Firmware being 2.60.37. I would sugest that you revert to the standard released firmware.


NOTE

if the gen is running and you then change the start figure, the STOP figure would have to be meet first before it would start again or vice versa