I have a Victron easy solar 24/3000/70/50, we are using power assist but vacuum cleaner trips the generator, we have set our input current limit to suit generator size and also tried dynamic current limiter.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I have a Victron easy solar 24/3000/70/50, we are using power assist but vacuum cleaner trips the generator, we have set our input current limit to suit generator size and also tried dynamic current limiter.
Use the colour control and put the input current limit down even further. Most generators derate at altitude and temperature, or it has a not so great voltage regulation unit. So it is possibly not able to make its rated power.
We have a 2.2kva through our 3kva easy solar and manage the vaccuming fine. You don't mention the size of your generator or vaccum, so just guessing here, ours is set a 4 A input. It also trips out if we go higher, but then it's not a great generator; in theory it should be able to give 10A in reality it is very different.
In good sun though with the right amount of solar in installed you will never need the generator to run the vacuum.
Thanks @Alexandra, I have a 3kva generator and yes after a number of tries I have reduced my current limit from 12A to 6A and it now works, but, it also reduces the capacity of my generator by half, anything over 6A come from my batteries which I’m trying to charge and run the house. My 3kva generator will work with normal load up to 12A but won’t handle the startup load of my vacuum cleaner and sometimes my pressure water pump.