question

jonatanjensen avatar image
jonatanjensen asked

Is 233V 19A in each input (3pc MC4) ok? Smart Solar MPPT 250/100 48v!

I have 9,9kW panels. 36pc 275W Voc38,7V Isc9,17A.

That's all for Off-grid:

Quattro 10000 48

Smart Solar MPPT 250/100

BYD Premium LVL 30,8kWh

venusGX

MPPT ControllersMPPT SmartSolarsolar sizing
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
klim8skeptic avatar image
klim8skeptic answered ·

Unless you never get frosts, your array will go over 250 volts at temps of 0c (32f).

Please use the Mppt Calculator.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jonatanjensen avatar image jonatanjensen commented ·

2020 until now i had 6panel strings also but now i need to double it. was hoping that this will work as well.

0 Likes 0 ·
Vance Mitchell avatar image
Vance Mitchell answered ·

So long as temperatures never caused the panels to exceed 250v the controller could handle it.

You would however be unable to use a lot of your solar capacity as that controller is only rated to 5800w @ 48v

I would consider adding another controller or reducing the number of panels. 24 panels (6s4p) would be the maximum I would connect to that controller.