Hello,
how can I add a button to activate/deactivate the relay implemented in the Cerbo GX on the screen of the Touch GX without using see submenu?
Is there any possibility?
Thanks
kind regards
Ulli
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hello,
how can I add a button to activate/deactivate the relay implemented in the Cerbo GX on the screen of the Touch GX without using see submenu?
Is there any possibility?
Thanks
kind regards
Ulli
Hi,
do you mean how can you toggle the relay without using the relay menu in the GX?
@Wiedholz , I notice this question hasn't been answered and thought I might suggest something that is not ideal but may be an option you may consider.
When the Cerbo has a generator auto start enabled, a manual button appears on the touch 50 allowing you to manually start the generator. One posssibility is to enable generator auto start, set parameters that will never actually start the generator and use the generator manual start button to trigger the relay. The generator autostart could be set to start on SOC of 110% for instance which will never actually happen. It will provide the manual start button however that can be used. It is not perfect becasue it will be labelled Generator start but it is a way to have a button to close a relay.
I hope this helps,
regards,
Trevor