Multiplus 24/5000 not entering bulk. Charges the battery on float. (solved)

I have an offgrid system with a a Multiplus 24/5000 , MPPT 150/35, BMV 700, CCGX and a Fronius primo on ac output. The battery discharges up to 83% SOC (min. voltage around 24,3V) during the night and the next morning does not enter bulk phase. It stays in float until the battery is fully charged.It happens with DVVC and without DVCC. The "Enable battery monitor" box is not selected in the VEconfig general tab as the BMV is more accurate. The only way to start a charge cycle is to restart the multiplus. Any ideas?

MPPT Controllers
2020-07-14-3.png (106.3 KiB)
2020-07-14-2.png (77.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Vangelis Beligiannis avatar image
Vangelis Beligiannis answered ·

I finally found what is going wrong!

The Multiplus does not start a new charging cycle if the battery voltage does not drop under a certain value. So I was not discharging the battery in order to trigger a new charging cycle.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

barney9304 avatar image
barney9304 answered ·
I would check whether it's because your on adaptive charging as it doesn't seem to like off grid scenarios as much.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Vangelis Beligiannis avatar image
Vangelis Beligiannis answered ·

Thank you!

I changed it but nothing happened.