I would like to inquire the required AC Out 1 protection needed to protect a grid connected Victron 5kVA unit.
Thanks
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Good day all,
I would like to inquire the required AC Out 1 protection needed to protect a grid connected Victron 5kVA unit.
Thanks
Are you working with a 230v or 120v model?
In general we work it like this;-
5000 ÷ 230 =21.7A so a 20A or 25A breaker will work for the main output of the inverter.