Required AC Out1 protection for Multiplus

Good day all,

I would like to inquire the required AC Out 1 protection needed to protect a grid connected Victron 5kVA unit.

Thanks

victron products
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@DanePB

Are you working with a 230v or 120v model?

In general we work it like this;-

5000 ÷ 230 =21.7A so a 20A or 25A breaker will work for the main output of the inverter.