BlueSmart IP22 - 0.0A while loading

Hi - my IP22 shows that it is loading with 14,44V but with 0.0A. I am not an expert but this seems to be a problem. Also my battery monitor shows no incoming power. I now disconnected everything (only the IP22 is connected) and same result.


There is only one battery connected right now.


Any hints?


charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Mark avatar image
Mark answered ·

Please check the fuse and anything else in the circuit - I suspect an open circuit somewhere...

You could also try to measure the voltage at the end of the DC leads with a multimeter or try to run a 12V load/light.

If these tests all turn out good then your battery is probably dead and has an internal open circuit.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mimbeck avatar image
mimbeck answered ·

Current status: a fuse in the + wire to the battery was not working correctly. Problems seems to solved. Thanks!