Multiplus 2 stops accepting the grid and then overloads ESS

Hi,

We have a customer that's their Multiplus 2 occasionally(3 times in the last month) stops accepting the grid and then goes into overload and cuts out. Meaning they lose their emergency circuits, while the grid powered circuits stay on...the opposite of what we want.

When the overload takes place, there is not a lot of current being drawn through the inverter.

Has anyone experienced this?

Voltage and frequency input is normal.

Thanks Dean

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Jaco Reinecke avatar image
Jaco Reinecke answered ·

Hi,

I have seen the same. Only happens at low loads.

Two things that are in the pipeline to be checked:
1) The distance from the street transformer is quite a distance, so it could be AC Ripples, to be tested.
2) The pre-paid meter is misbehaving, to be checked.

Client disconnected from the grid in the meantime, running inverter in an off-grid scenario unitl the above can be checked, ruled out.