Victon EasySolar - Generator current limiting from the CCGX controller

Hey, is it possible to Limit the generator input current from a CCGX without using veconfigure


EasySolar All-in-One
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Mark avatar image
Mark answered ·

Yes you can change the input current limit from the GX device, providing that the 'Overruled by remote' checkbox in VE.Configure is enabled.

Select the MultiPlus/Quattro from the device list, then update the 'Input current limit' as desired.