quatro 8kw

i have a system what contain one 8kw quatro, 150/100mppt , 21 solar panel 325w, 8 battery 220ah, and one color GX . Maxim value of production 5.5kw for more the 6 hours pe day.

I like to push in grid the exeses when i dont have consumption. The engineer(from the grid) from Romania is asking me and to proves/show to him how the quatro is reacting on variation of input voltage and variation of frequence and if is stopping on this problems(variation). He wonts in writing to see and physical.

thx for help.

Help
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@apophis

Do you have a GX device connected and is it transmitting to the vrm? You could use the csv data logging for that. Or just show him in the screen.

The .csv data shows grid voltage and frequency as well at the victron as well.

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ commented ·

https://www.victronenergy.com/upload/documents/Certificate-G59-3-1-MultiPlus-and-Quattro-3kVA,-5kVA,-8kVA,-10kVA-and-15kVA.pdf

https://www.victronenergy.com/upload/documents/Certificate-IEC-62116-(2014)-Test-procedure-for-islanding-prevention,-all-Multis-and-Quattros.pdf

Victron also have certification for various grid codes. Not sure what Romania have as code

https://www.victronenergy.com/inverters-chargers/quattro#certificates

There should be some local regulations for grid feedback though so the Engineer should know these.

Antiislanding is an issue for safety reasons. There is a built in mechanism in the quattros. Some countries require an external device for this still though.

0 Likes 0 ·
apophis avatar image apophis Alexandra ♦ commented ·

kkk the certificate is writing the value but not that he is disconecting from the grid for this kind of problems

0 Likes 0 ·
apophis avatar image apophis Alexandra ♦ commented ·

i found but in first certificate my quatro is mising from the values onli 10kw and 15kw has the values?

0 Likes 0 ·
2 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

You will need a GX device to setup an ESS.
Maybe you will need an energy meter and depending on you local laws an anti-islanding relays.

https://www.victronenergy.com/live/ess:start

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

apophis avatar image apophis commented ·

i forget to write i have a color gx and in my contry they are changing the laws every year , even they dont know what to request from me.aaaa every part of the contry is diferent. to be more exact they refuze people like me to deliver the exes of power to the grid

0 Likes 0 ·
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @apophis

you can download all applicable certificates here:


https://www.victronenergy.com/inverters-chargers/quattro#certificates