question

fandm avatar image
fandm asked

Quattro 48/1000: combining 1 battery bank to 4 quattro's: 3Phase + 1 Single phase

Dear all

Can I expand an existing 3phase Quattro system with 3 quattros 48/10000 and 1 battery bank with an extra single quattro 48/10000 for an extra single phase load connected to the same battery bank.

Thanks for the feedback

Jo

battery charging3 phasesystem design
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
jwfrary avatar image
jwfrary answered ·

hi,

wouldn’t be a supported architecture.

You could I suppose use it purely as an inverter the single phase and leave the charging to the other units. But you might as well use a Phoenix inverter instead.

Otherwise it’s an independent system

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jwfrary avatar image
jwfrary answered ·

However, just thinking about it, and I haven’t seen it, but I’m not sure if your allowed to have an uneven number of quattros on one phase, so you could take your single phase sockets from that and it would all network together.