Hi , I have 4 x Enersys 12T105F 105 Ahr batteries in parallel being charged by my blue solarsmart 100/50.
Float voltage is specified by Enersysy as 2.280V pc at 20 degrees C & 2.265V pc at 25 degrees C.
In the smart app ...What should I set absorption voltage to? The temperature correction to? or is one of the presets a correct one to use?
I know that 4 batteries in parallel isn't ideal ,and I will likely change to a 24v setup with 2 in parallel x 2 series and have a 24-12v Orion converter to run my 12v system.
Solar panels are 4 x 250 W setup in 2 strings of 2 in parallel so I have plenty of incoming power.
I have noticed at the moment (with a test load of 25W on 100% of the time) that I reach end of bulk charging in 3.45hrs,Absorption afte 2hrs then into float. Late in the afternoon it goes straight back to Bulk mode....Is this because I have the 25w load running?