question

jurjenhoekstra avatar image
jurjenhoekstra asked

Ignore AC and DVCC

I have recently installed solar panels on my motoryacht. I am now looking for the most economical use of the solar panels, also in order to reduce the cost of shore power. The electrical system has mainly Victron components, except the panels and battery: Quattro 8000/200, Venus GX, MPPT 100/30, 720 Ah tubular plate batteries and 2 x LG Neon R 370 Wp panels, latest firmwares.

I have studied all the manuals and looked for answers on the community site. Although I see similar setups, I still do not have the ultimate answer on how to use the panels the most economical, either by using Ignore AC, DVCC, lower float voltage or a combination of these.

I fully understand how Ignore AC in VEConfigure works and have now set it up according to below screenshot:

I have been to the yacht today and have tested it with several loads. When using heavy load, the Quattro will deliver the power instead of drawing it from the battery, so it does not unnecessarily drain too much, which would take forever for the panels to charge back into the battery. There is a certain amount of equipment that draws about average 200 W, so in a day I will loose 4.8 kW. On sunny days the panels will charge with about 4.8-5.1 kW. So on cloudy days and near winter time the batteries will slowly deplete and when voltage reaches 23.5 V, the Quattro will kick in and charge (with max 100 A) up to when bulk is finished (85 % SOC). I might change that in wintertime to when absorption is finished, as the batteries need to be fully charged every once in a while. So far so good.

The manual of the MPPT states that the DVCC function will result in the MPPT being an active controller in the system. "For systems with lead batteries, DVCC offers features such as a
configurable system wide charge current limit, where the GX device actively limits the
inverter/charger in case the solar chargers are already charging at full power". I have tried the DVCC feature (without Ignore AC) with a setting of 100 A for max charging and shared voltage, current and temperature sense.
I have observed the behaviour of MPPT and Quattro for a long time and my impression is that the MPPT does not always do what it should. I can see the Quattro charging with high amps and the panels with relatively low. When I switch off the shore power, the panels immediately jump to a much higher charge, so the panels are under DVCC not used with maximum capacity. I would also expect that when batteries are full and loads are low, while panels can produce more than the load, that the Quattro might stop charging all together.

An expert advised to lower the float voltage of the Quattro with 1 V, After lowering that setting to 26.6 V, I saw this morning at around 08.00 hrs that the Quattro stopped charging. Not completely sure why?

I have gathered my thoughts and I think I have to options: 1) use Ignore AC and 2) use DVCC. With option 1, it will deplete the battery more and I think the panels are used most economical, but I need to make sure the batteries are getting a full charge every once in a while. With option 2, the batteries are kept a full charge (100 %)., but I have the impression the panels are not used to the max and the Quattro will only stop charging when the voltage of the batteries is higher than the 26.6 V. Which brings me to the question do I also need to lower the absorption voltage in order for the Quattro to stop charging when in absorption fase in order to get the max charge out of the panels? I find lowering these setting in contradiction to the DVCC manual: "Limit charge current. This is a user-configurable maximum charge current setting. It works across the whole system. MPPT Solar Chargers are automatically prioritized over the mains/generator".

By the way: I use the AC out 2 of the Quattro for heavy users, with the intention that when I loose shore power (while sailing [do you actually sail, drive or operate a motor yacht?]), it automatically switches of the heavy consumers and I will not unnecessarily deplete the batteries. With Ignore AC while still in the harbour, I loose the heavy consumers as the Quattro needs AC on either AC In 1 (generator) or AC In 2 (shore power). I probably have to rewire the heavy consumers to AC In 1.

My questions:

1) Why does the Quattro stop charging when lowering float voltage when panels are charging?

2) Do I need to lower the float voltage in order for the Quattro to stop charging while enabled DVCC?

3) Why is DVCC not using maximum available charge from the solar panels?

4) Do I also need to lower the absorption voltage while DVCC enabled so the Quattro stops charging in absorption fase to maximum use the charge of the panels

5) Can I, or should I, use DVCC in combination with Ignore AC?

Any comment, suggestions, answers are welcome.

I have also published about the installation of the electrical system and the solar panels on my weblog (in Dutch, but has Google translate button): www.xanthiona.com .

VEConfigure 3DVCCmppt chargingac out 2
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jurjenhoekstra avatar image jurjenhoekstra commented ·

In the above I asked some questions about Ignore AC in relation to DVCC. I also stated that when using the virtual switch to enable Ignore AC, that I loose the AC out 2 of the Quattro to which my heavy consumers are connected. The essential purpose of AC out 2 of the Quattro is that it disconnects when there is no shore power or generator running in order not to drain the battery. But when the Ignore AC has temporarily disabled my shore power and while I am still in the harbour, I might still want to use the oven, wasmachine, dishwasher or boiler.

Thanks to the Victron Community I found a solution for this. I found some example on how to use assistants to enable this. I also use the assistant to Ignore AC, in stead of using Ignore AC through the Virtual Switch. In the assistant the programmable relay for start/stop generator is used by using the same conditions as in the Virtual Switch to Ignore AC, followed by the assistant to switch on AC out 2 under certain conditions. I may still have to tweak the settings a bit. The 2400 W is still too high, should maybe be 2000 or even 1800 W.

0 Likes 0 ·
2 Answers
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @jurjenhoekstra

your long post is difficult to churn through, it is better to ask one question per post. But I'll try to answer some things:

The manual of the MPPT states that the DVCC function will result in the MPPT being an active controller in the system.

-where does it state that? it's usually the Multi that's in control (except when you have a battery with bms that controls charge)


1) Why does the Quattro stop charging when lowering float voltage when panels are charging?

I cannot answer that without knowing voltages and settings, but when charge voltage of inverter is lower than charge voltage of MPPT that is expected.

2) Do I need to lower the float voltage in order for the Quattro to stop charging while enabled DVCC?

That doesn't work, because when you use DVCC, all chargers use the same setpoints (except when using ESS + feed-in)

3) Why is DVCC not using maximum available charge from the solar panels?

DVCC is not using anything, it's a setting

4) Do I also need to lower the absorption voltage while DVCC enabled so the Quattro stops charging in absorption fase to maximum use the charge of the panels

same answer as Q2

5) Can I, or should I, use DVCC in combination with Ignore AC?

you can if you want.


did you read the manual on DVCC?

https://www.victronenergy.com/live/ccgx:start#dvcc_-_distributed_voltage_and_current_control

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jurjenhoekstra avatar image jurjenhoekstra commented ·

Thxs @Daniël Boekel (Victron Energy Staff) for your answers on my Ignore AC and DVCC. In the beginning I stated that I read all the manuals and studied similar cases on the Victron community and that the manual of the MPPT mentioned the feature of DVCC. It is actually in the manual of the CCGX/Venus GX.

In relation to question 3: Even though it DVCC is a setting, I observed when enabled that available solar energy is not used at it's maximum. When I switch of the Quattro, I can see immediately a big jump in the charge current from the panels. I have a friend in the harbour with nearly the same set up and yesterday we set up his system as well with DVCC and saw the same behaviour. So our conclusion is that enabling DVCC does not use the solar panels at it's maximum. We have now both enabled Ignore AC with certain settings.

In relation to question 5: Ignore AC seems to be the way to go for maximum use of the solar panels. What is the additional benefit of DVCC when using Ignore AC for those moments when the Quattro does kick to charge?

0 Likes 0 ·
Daniël Boekel (Victron Energy Staff) avatar image Daniël Boekel (Victron Energy Staff) ♦♦ jurjenhoekstra commented ·

about solar performance: this is probably because of lower charge voltage settings in the Multi, enabling DVCC sends the same charge voltage setpoint to the MPPT's.

When AC is connected, without ignore AC the system will charge from Multi, so less solar input.

DVCC doesn't have to benefit anything but can be helpful. It's up to how you use the system if it is helpful (with lead-acid batteries at least)

0 Likes 0 ·
erichabg avatar image
erichabg answered ·

@Daniel Boekel

Unfortunately, in my experience, when DVCC is active, a reduction in charge current (via modbus register 2705 or the corresponding nodered node) not only down regulates the Multiplus, but unfortunately also the MPPT. Even when the voltage settings of the Multiplus and the MPPT are the same. It is a pity that there seems to be no possibility to regulate this separately.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources