question

sebastianlehmann avatar image
sebastianlehmann asked

Can DC coupling Multiplus I or II Inject to grid after battery is fully charged?

Can DC coupling Multiplus I or II Inject to to grid after battery is fully charged?

how to NOT overchage the battery?

does the injection can be at full MPPT power posible when sun available?

Best Regards

dc system
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
ejrossouw avatar image
ejrossouw answered ·

Hi @SebastianLehmann Yes, The Multiplus is bi-directional and when connected the grid via ACIN and configured with ESS to feedin-in, the solar will first be supplying loads, then charge the battery and excess can be sent to the grid. Charger parameters are configured for bulk, absorbtion and float to avoid overcharging and the MPPT will reduce charging power as a result or provide the loads with whatever solar is available.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic