My current system:
1 x Quattro 48/15000/200-100/100
4 x Delta Gel Batteries GX12-200 (12V, 200 Ah)
48 x 150W Solar panels
2 x BlueSolar MPPT 150/70-Tr/MC4
Color Control GX
My problem:
Just installed and connected Quattro unit keeps switching over to inverter operation all the time even under load less than 1kW.
I had the same problem with my previous MultiPlus 48/5000/70-100 about 4 years ago. Without Solar panels it worked perfectly, but right after I connected my first solar panels and activated ESS, it started switching over to inverter mode, resulting in overloading. I have weak grid in my village – rather low transformer, so that when someone switches boiler or other heating device, voltage drops to 200V and below. That’s why I installed the stabilizer (Ortea Vega 1500-15 / 1000-20 (15kVA/10kVA – 2 operation modes), but it did no help to eliminate the problem of switching over to inverter operation. What really helped was a new firmware, which you released at that time – right after updating my Multiplus started working perfectly.
It continued before Sept 2019, when I installed the 2nd Multiplus to work in parallel, because I needed more power. But I could not stabilize their parallel work, what I described in details here: https://community.victronenergy.com/questions/46810/2-multis-in-parallel.html
Now in order to get back to normal operation, I bought Quattro 15000, thinking that it will work as good as Multiplus 5kVA in standalone mode. But it does not. I just disconnected my perfectly working Multiplus 5kVA and connected with the same wires Quattro 15kVA. And the problem returned: I have the same abnormal operation: https://youtu.be/aQsTwFqT24g
Dear Victron team,
Can you help out by releasing the next firmware for Quattro 15kVA, similar to the one you released for 5kVA devices? This really solved my issue last time?
Or can you advise me anything else?
I spent so much money and time, trying to figure out what to do and tried almost everything, except direct programming and coding, going beyond capabilities of VE Config. This could really help me, but in order to do it, I’ll have to learn how to do it properly, what will kill lots of my time, which I don’t have.
I’m deeply disappointed. Can you give me a glimpse of hope?