So commissioned a new system a few days ago, it’s standalone with 4x200ah “cranker” batteries. Has ESS and 4kw of panels ..
Ran a “grid fail” test with a load of 2376w (as according to the console) and it went straight to overload and shut down the ac out for long enough to reset every computer. This didn’t happen at 2100w(ish)...
Ambient temp was 21C and batteries >90% charged.
Thought these units are supposed to handle 3000W for a short time and 2400W continuous at 25C?
Thoughts?