Hi all, I've got a Multiplus II 48/3000 which I intended to run with a 14S lithium-ion battery bank.
This will however be a bit of a challenge with the battery bank physical layout and super messy wiring.
Not sure why I didn't discover the max input voltage rating of 66V on the MP2 before today, but moving from 14S to 16S will really help a lot. I do not plan on running the lithium cells higher than 4.0-4.1 volts anyway - which means I'll stay within the 66V max.
Is there any reason you could think of that suggest I should stick to the plan and go with 14S?
Both 14 and 16S allows me to stay within a nice range for the lithium-ion cells (3.2-4.1V)
The only two issues I can think of, are that I have to run triple solar panels to stay above the system voltage and that I may be pushing the spec of some standard fuses?
Thanks!