Which fuse for cyrix ct 230?

If I put a of 250A is a problem?

I have found automatic switch but of 250A, can I use?

Thanks

Regards

Alex

fuses
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
cquinones (Victron Energy Staff) avatar image
cquinones (Victron Energy Staff) answered ·

Hola @Alexx , Perdona por el retraso debido al Covid-19 y gracias por esperar nuestra respuesta. Te respondo en Español en este canal.

El fusible depende de la corriente máxima que esperes en ese circuito , por seguridad dale un 20% de margen de más . Más info en nuestro "wiring unlimited " en Español ,punto "4.4 Fusibles y disyuntores" https://www.victronenergy.com.es/upload/documents/Wiring-Unlimited-ES.pdf