smart solar 75/15 PV input 45 volts 10 amp? is that ok

I have 2 170 watt panels in series. So that 45 volts max and 9.24 amps. I have a Victron 75/15 charge controller. Even though i'm over on wattage according to specs it makes no sense. I am way under voltage and under amperage. You think i will be ok or should i get 100/20 charge controller. My bank is 110 ah.

charge controller compatibility
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Patrik Kall avatar image
Patrik Kall answered ·

Thats perfectly ok, the Victron MPPT will simply ”ignore” the extra wattage when/if it occurs.

Normally you only get maximum watt/volt/amp when there is full sunshine and cold weather, preferably like 0C (32F) or lower as power from the panels decrease with higher temperature.

The higher the voltage is, within the MPPTs limits, the earlier the panels starts to produce