Multiplus 2 5000 produce reactive power

I use the MP2 in ESS mode 3 via Modbus to feed back power to the grid. I watched that sometimes the MP2 produces power peaks if the power setting is low for example 100W. In some cases this results in high reactiv power output of the inverter measured values 1200VAR capacitive. The inverter stays in this mode until i raise the power to higher values > 1000W than it works stable until the next sporadic peak (there can be hours in between) puts the inverter in that reactive mode. The MP2 was excanged with another MP2 with the same result. I hope that victron have a solution for that problem. This instability is not acceptable grid inverters.

Multiplus-IIESS
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

spudgun avatar image spudgun commented ·

Did you ever come up with a solution for this problem? I am experiencing the same thing and I am not sure how to resolve it.