Generator state start/stop CCGX

Hi,


I have some problem running the generator from CCGX. The generator is the mains and connected at AC1 input on the Quattro's. The generator start/stop signal is connected to te relay terminal on CCGX. We want to use the relay to close when there is no need for generator and open when the generator is needed.

This is what i have done on the CCGX:

Settings -> System setup -> AC input 1: Generator

Settings -> Relay -> Function: Generator start/stop

Settings -> Generator start/stop -> Settings -> Detect generator at AC input.


I believe I have done it right, but when the generator is running the Generator start/stop state shows "stopped". I beleive this is the problem.


Can anyone help?


CCGX Color ControlGenerator
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
harold avatar image
harold answered ·

Is it running, because of it has been triggered by the CCGX?

Or did you start it at the Generator?

The State in the VRM only indicates the status from the CCGX triggers

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

orjolsen avatar image orjolsen commented ·

Hi,

Found the problem. Needed to reverse te signal to generator. Connected a external relay and, problem solved.

Thanks anyway.