On the MultiPlus II, is it possible to completely disable charging batteries from the grid and only use solar?

I'm currently planning the following configuration below


In this scenario, is it possible to completely disable charging batteries from the grid via AC-In and only use the solar panels connected to the BlueSolar & excess power from the PV grid-tied inverter connected to AC-Out to charge the batteries?

Many thanks in advance for any help.

Multiplus-IIMPPT Controllersbattery chargingsolarFronius
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Rob Duthie avatar image
Rob Duthie answered ·

Hi

Yes it is, just setup the ESS correctly to suit, this is how mine works, and only charges from the PV not the grid at all. Read the ESS manual for the CCGX etc.

Regards

Rob D

NZ

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Meine_Energiewende avatar image
Meine_Energiewende answered ·

Just a question regarding that setup: is a 15 kW Fronius suitable for a 3 phase setup regarding 1:1 rule ? So the rule applys to the wohl 3 phase setup and not a single MP-II ?

I ask this because i will update my setup to 3 phases soon and i use a Fronius 4,5-M3 till now. Am i able to use 2 more of these guys in the future ? (will be near that 15 kW Limit)

Thx

Jens