Have a paired 12/3000 multi split phase install that is seeing occasional overload errors - this is somewhat expected as there are multiple cruisair units that can sometimes start close together. They all have soft starts, but can still see 200ms at ~35-40 amps.
The odd thing is it will shutdown when it happens late at night, they shutdown. When it happens during the day it just notes it and plods along. There other loads that vary and there are water heaters on the 2nd output of the multi. Power assist is enabled, and Should be able to carry everything for brief moments.
What is the shutdown vs. warning criteria on overload?