Hi
When programming my assitant rules, using SOC, must SOC of the VE.BUS be configured (via VEconfig)?
Or will it use SOC from the system CCGX (BMV)?
If I switch on SOC in the VE.Bus, I dont see SOC in the graph in VRM, is this correct?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi
When programming my assitant rules, using SOC, must SOC of the VE.BUS be configured (via VEconfig)?
Or will it use SOC from the system CCGX (BMV)?
If I switch on SOC in the VE.Bus, I dont see SOC in the graph in VRM, is this correct?
Hi @Harold
You need to enable battery monitor in the Multi, and in the GX device select the BMV as battery monitor, the BMV's values will than be written in the Multi, and any assistant will therefor use the BMV's values.