Two MultiPlus in master-slave config and Two-Signal BMS Support

Hello,

I'm using two MultiPlus 12/3000/120 16 in a master-slave - configuration connected to an other lithium battery and BMS.


Do I need to connect the BMS signal (allow to charge -> Aux IO / allow to discharge -> TempSense) to the MultiPlus master only, or is it need to connect the BMS signal in parallel to master and slave inputs and do I need to load the 'Two-Signal BMS assitant into master and slave?

Thanks in advance and b.r.

BMS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

Load the assistant into all MultiPlus'. Connect the BMS wiring to one of them. I'd like to connect the BMS signals to the Master one

https://www.victronenergy.com/upload/documents/Manual-Connecting-other-lithium-battery-systems-to-Multis-and-Quattros-EN.pdf