question

Craig Myatt avatar image
Craig Myatt asked

Multi 3 phase question about VE Bus Configurator

If anyone may know, in the VE Bus configurator software for 3phase Multi systems, is it necessary to select, as well as 3ph via the 3phase button on the software, 3 AC inputs? To reflect the three phases L1, L2, L3 coming in? It is a bit unclear...in the help file...

Multiplus-II3 phase
3phase.png (42.1 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Typically 1 AC input, with 3 phases L1, L2, L3.

You can see the effect of selecting multiple AC inputs in the demo mode.

I also recommend completing the 3 phase online training in Victron Professional.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Craig Myatt avatar image Craig Myatt commented ·

I have done the training...very good vid by the way, guy. and I guess that makes sense now...which means, as I did setup the 3 phase Multi's, pretty much as per your training video, using the configurator, is correct: with L1, L2, L3 coming in (1 AC input, as you said) ...and each of the multi's then corresponding to those 3 phases. Thanks Guy,

0 Likes 0 ·