michelp avatar image
michelp asked

Multiplus-ii Gx strange data in ESS mode 3

Hello,


I start to run my multiplus-ii Gx in ESS mode 3 and i have some strange power data on the console interface

The control loop setpoint is equal to 0

When I look on the LCD I have


Grid=0W, Output=-126W, battery=78W

The questions:

Does the console data are reliable ?

What is the output Power (-126W) ?

Michel

Multiplus-IIESS
testpv.png (35.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
michelp avatar image
michelp answered ·

I have understood the issue

Due to lack of connexion on the external tore sensor (the click is'nt done)

What i am also understood there two grid

One is the external sensor (the tore)

One is the AC_in1 of the Multi

The target of the internal control loop is the AC_in1 of the multi

Nice I go to use Mode3 now