Battery capacity settings

In VE Configure 3, when you enable battery monitor, you need to supply your "Battery capacity" in Ah. If you have a 48V system and 4 x 200Ah batteries do you set it as 200Ah or the sum of all the batteries (800Ah) ? I have checked the manual and posts and cannot find absolute clarity on this.

Many thanks.

BMV Battery MonitorVEConfigure 3battery capacity
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

If all your batteries are connected in series (I guess you do), then your bank will be 200Ah. 200x48 = 9600Wh

If all the batteries are connected in parallel, then your bank would be 800Ah. 12x800 = 9600Wh.