Can anyone advise if the Multiplus 48/800/9 inverter/charger be used to establish a micro-grid ac coupled with microinverters without the grid in the same way as the Multiplus ll.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Can anyone advise if the Multiplus 48/800/9 inverter/charger be used to establish a micro-grid ac coupled with microinverters without the grid in the same way as the Multiplus ll.
Hi @Electrix. The multi 800 is just smaller than the 5, but has the same functionality. Keep in mind to adhere to the 1:1 rule with ac couple systems: https://www.victronenergy.com/live/ac_coupling:start
I think we are referring to different units. By the 5 do you refer to the 5000, as the largest model in that series I refer to is 1600. Further I can find no info on the victron website inferring that the Multiplus 5000 has this capability. I can find no unit other than the Multiplus ii that has this capability.
Yes I’m referring to the 5000va Multiplus. The Multiplus ii has an extra ac disconnect built in to comply with various grid codes, but apart from that all Multis have the same functionality, from 500Va all the way to the 5000Va. They can all be ac coupled