We have a system setup as follows:
Multiplus II 48/5000/70-50 firmware version: 469
CCGX running ESS firmware version v2.42
BMV-700
Grid Meter
MPPT 150/70
Everything running latest firmware.
We only recently upgraded from a Multiplus 3000 which we ran for more than 5 years, all settings have remained the same on the new Multiplus II in terms of the ESS settings etc.
We are having a strange issue which we are struggling to diagnose. When there is a grid failure (load shedding as it is euphamstically called in South Africa) the Multiplus II immediately shuts down and turns off. Plunging us into darkness like the rest of the country.
Battery voltage according to the BMV and CCGX is still more than ample at above 50v when this happens. Loads on the Multi are under 800w.
If I then go and use the manual switch on the bottom right of the multi, I can turn it off and on again and it will go on for less than a minute and then shut completely off again.
If I unplug the ethernet cable that runs from the VE.Bus on the multi to the CCGX, the Multi starts again and runs perfectly in inverter mode and powers the load during the load shedding. As soon as I reconnect the cable to the VE.Bus port on the multi, it immediately shuts down again.
No error reports, no alarms.
This leads us to believe this is some type of communications issue between the multi and the CCGX.
I dont believe there is anything wrong with this cable as it worked 100% for more than 5 years between the Multi and the CCGX and it also works 100% when the grid is on.
If there is NO grid failure, the Multiplus II runs happily for days on ESS settings using the generated PV power to supplement house loads etc.
This issue ONLY happens when the grid fails.
Has anyone seen this issue before? The site has been on the VRM for many years if anyone from Victron wants to connect and check it out.