Can the Skylla TG Charger 48v/50a accept more than one input?

I want to connect a 48v DC generator (Integrel) and shore power to the charger. Will this charger accept two charging sources? Would not have both running at the same time.

Skyllaintegrel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
markus avatar image
markus answered ·

Hi,

you can have several charging sources, however, they should all be connected to the battery, not to the charger. Only 230V 50/60Hz should be connected to the chargers input.

It should also be no problem, to use both of them at the same time. They will support each other, just in case.

Regards,

Markus