question

mfortinberry avatar image
mfortinberry asked

EasySolar 48/5000 shore power conversion

I will have the EasySolar 48V/5000kVA on a boat wired for European 230VAC.

When in the US, if plugged into 50A shore power (240VAC/60Hz), will the system effectively convert that to its normal 230V/50Hz output?


Or... do I also need something like a Charles Industries Isolation Transformer installed inline of the shore power?

EasySolar All-in-One
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Johannes Boonstra (Victron Energy Staff) avatar image
Johannes Boonstra (Victron Energy Staff) answered ·

You mean you want the 48/5000 Easysolar to be connected on 120Vac/60hz?

Well certainly no Charles industrie products are needed ;-)


When you want an isolated step up/down transformer, please have a look here

https://www.victronenergy.com/upload/documents/Datasheet-Isolation-Transformers-EN.pdf


Whe you want to be also able to hook up to splitphase connections (120/240Vac ) then please have a look here

https://www.victronenergy.com/upload/documents/Datasheet-Autotransformer-32A-and-100A-EN.pdf



Ps in both cases , the input frequency is equal to the output frequency which isnt a problem normally but the Easysolar must be set to this frequency.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.