Quattro multiplus digital input spec

Hi.

I have a system on 3 quattro 10kw in a 3 phase system, solar chargers, BMV, wind generator, CCGX and will now install a litium battery.

I have 2 questions:

1: I cant find any spec on the digital inputs that is on the quattro in the manual. Are they 0-5V analog, 24/48VDC digital, both? (for the BMS control of the quattro)

2: i want to se the charging of the wind generator in the CCGX, like i se the solar charging separate from everything else.
Today i use the funktion "Has DC system" in the CCGX but it must be a better way for this?

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Jimmy Henningsson

1. the digital inputs are indeed 0-5v, and when a input is pulled to 0v it is registered as 'closed'

2. unfortunately no other way to visualize this wind input in the CCGX