Swaleh Hassan avatar image
Swaleh Hassan asked

Quattro 10va overload issue

Hi,

We recently installed a Quattro 10kva for power backup system. Been working for a month then today it the overload LED came on.

We removed the loads and still has an overload LED. When switched to charger still has the overload LED.

We have tried to update the firmware but still in vain.

Kindly assist with what could be the problem






MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
boekel avatar image
boekel answered ·

It sounds like it is broken, and has to be fixed by Victron...

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Is the unit working and supplying power?

It also appears that you still need to clear the overload alarm messages from the CCGX by pushing the centre button in that notifications screen. You can tell as there is a tick box¸Â where it says menu down the bottom right.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Swaleh Hassan avatar image Swaleh Hassan commented ·
Thank you. The unit is not supplying power and it just shows the overload LED. Thank you also for the info on clearing the overload alarm message
0 Likes 0 ·
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi Swaleh; sorry to hear that the unit is probably broken. Please contact your dealer to have this sorted. See also process here:

https://www.victronenergy.com/support

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources