question

Chris Kennedy avatar image
Chris Kennedy asked

No input current

I just installed the BMV 700. I'm not getting an input reading for amp hrs. It tells me how much I'm using, but not what's going in. This is a solar set up

Thanks


dc system
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

Is the negative wire of the solar charger on the right side of the shunt(loads chargers) or is it directly connected to the battery?

At the side labeled with "battery only" should only be the battery minus and nothing else should be connected there or at the battery minus.

All other negative wires must connected to the "load/charger" side of the shunt.