I just installed the BMV 700. I'm not getting an input reading for amp hrs. It tells me how much I'm using, but not what's going in. This is a solar set up
Thanks
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I just installed the BMV 700. I'm not getting an input reading for amp hrs. It tells me how much I'm using, but not what's going in. This is a solar set up
Thanks
Is the negative wire of the solar charger on the right side of the shunt(loads chargers) or is it directly connected to the battery?
At the side labeled with "battery only" should only be the battery minus and nothing else should be connected there or at the battery minus.
All other negative wires must connected to the "load/charger" side of the shunt.