Quattro 10k with ESS Grid connected / solar / CCGX.
Previous overload switched off system and due to lock out could not be re started without intervention by un plugging CCGX. Freezer contents lost as we were away.
Just now a year later same overload situation. No warnings - system tripped off.
Overload LED lit. Prior to event Voltage was 48v and load was around 500w. System was discharging as it was after sunset.
At 18.00 voltage dipped from 49.90v to 46.40v and current dipped from -11.40amps to -44.20 amps which was the event. Reset the quattro = 50.20 v and 0.10amps then it reverts to 48v and -7.60 amps which is normal.
No errors or warnings recorded.
The only loads to stress system would be well pump/ freezers no other loads with high inrush.
These loads are running all day without a problem.
So what causes a massive dip in current????