johnno63 avatar image
johnno63 asked

24/1600/40 voltage reading

What should the voltage reading between E & N and E & A be. I have a reading of 60 volts across both. Is this normal

inverter current draw
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

Im going to presume that this is a 120V output version?
For a single phase system, there should be 0V between Earth & Neutral. There should be 120V between Active and Neutral or between Active and Earth.